- Guest asked 7 years ago
Hello
On the 532 series units the condensers can be plugged and restricted easily. You need to clean the condensers with C02 . They need to be 100% clean to operate properly. We clean them by taking a wet towel and cover the top of the compressor and blow high pressure C02 through the condenser and the wet towel catches all of the dust. Many times we found impacted condensers that were just cleaned on the outside layer of the condenser. Then the unit continued to overheat and compressor extremely hot and shuts off on the overload all due to a dirty , impacted condenser. Also make sure the condenser fan motor is running and moving good air across the compressor. If all of this is done you may have a defective compressor. See technician guide below to verify compressor failure. Matt Ace technician
- AV Repair Help answered 7 years ago