THE DATA PLATE IS ILLEGIBLE FOR THE MOST PART. THAT MODEL NUMBER IS WHAT I THINK IT READS. I NEED TO KNOW THE CORRECT REFRIGERANT CHARGE TO WEIGH BACK INTO THE UNIT.
TX
- Guest asked 8 years ago
Hi. I have attached the tech sheet for your unit. IT does not state the refrigerant charge and I could not find the correct amount anywhere else either. I would guess that it takes 5.0 ounces give or take .5 ounces. The tech sheet does give proper low and high side pressures. You could dial in 5 ounces and then wait about 20 mins and check your pressures . Then you can remove or add refrigerant until your pressures read correctly.
- Brian, Ace Appliance answered 8 years ago