What are the most common problems causing a GE profile to no cool properly ie 33 degrees in freezer and 50 degrees in refrigerator

Model Number
PSC23SGPA SS
What have you tried so far?

Nothing

Request Resource Materials
Service diagnostics guide
0
0

Hello
Se e technician information links below. On a dual evaporator system with above normal temperatures in both sections would indicate a starved evaporator or ( Low refrigerant charge ) . Or a possible frosted coil with a defrost issue. Since you are getting 33 degrees in the freezer tells me your compressor is running and the inverter board is powering the compressor. I would remove the cover to the freezer evaporator to see if it has an even frost pattern, Or if you have heavy frost on the coil that would indicate a part of your defrost system is not functioning. If it is not frosted you will need to tap the system to determine if its a low refrigerant charge. Matt Ace technician