I CLEANED THE COILS TO THE BEST OF MY ABILITIES, BUT THEY WERE HARD TO GET TO. I MANUALY OPENED THE AIR DIFFUSER, AND CHECKED THE EVAP. THE EVAP HAD A CONCENTRATION OF ICE BUILD UP IN ONE AREA, BUT EVEN IN ALL OTHER AREAS. THE FANS ARE BOTH RUNNING FINE AS WELL AS THE COMPRESSOR. WHEN I LEFT I COULD ONLY GET THE FRIDGE TO 48 AND THE FREEZER TO 20, BUT THE UNIT WAS EMPTY AND ROOM TEMP WAS ABOUT 80. YOUR THOUGHTS? THANKS, TODD FROM NY.
- Guest asked 9 years ago
- last edited 9 years ago
Hello
From the description you are giving me and the symptoms, I am thinking you have a sealed system issue, a leak or defective compressor. Even if you have a plugged condenser you will not get a ball of ice on the evaporator. That is an indication of a starved evaporator coil. I would tap the suction line or process tube and check the refrigerant charge. I believe you will see a low refrigerant charge. Matt Ace technician