THIS CORSAIR CONDENSING UNIT KEEPS RANDOMLY SHUTTING OFF. IT WILL WORK FOR A FEW HOURS THEN IT WILL SHUT OFF AND WONT TURN ON AGAIN.

Model Number
FADC-042JAS
Serial Number
6495F220009965
What have you tried so far?

THE BLOWER FAN CAPACTIOR WAS BAD AND SO WE REPLACED THAT, ALSO THE COMPRESSOR HAS HIGH AMPS SO WE REPLACED THAT. AFTER EACH REPAIR THE UNIT WOULD TURN ON AND WORK FOR 6-12 HOURS THEN STOP AND NOT TURN BACK ON.

Request Resource Materials
Service diagnostics guide, Wiring diagram, Parts manual, Parts breakdown, Service bulletins, Service pointers, Job aids, Videos, Any available materials
0
0

Hello
Is the compressor and condenser fan motor shutting of ? If so, it sounds like you are losing 24 volts to outdoor condensing unit. We have had units with float switches in the condensate pump shut down the 24 volts to the condenser. I would make sure you do not have a plugged or restricted condensate drain. Also check the thermostat, especially if its digital. It could be programmed to shut down at certain times. Check the thermostat program. Matt Ace technician